Meter interfaces

Pulse outputs, wired M-Bus, Modbus RTU, P1 ports and analogue signals from the meters a site already has.

Most sites already have meters with a pulse output, M-Bus, Modbus or a P1 port. Reading them is often cheaper than fitting new sensors.

Start with the guide for the interface on your meter's label, then use its commissioning checks.

Meter interfaces

6 guides · about 59 minutes

  1. Pulse meters: dry pulse vs active pulse Compare dry contacts, open-collector and active voltage pulse outputs. Check wiring, isolation, pulse timing and scaling before connecting a meter. 14 min
  2. Pulse meter commissioning and reconciliation Commission pulse metering: output circuit, pulse weight, maximum rate, known-count tests, recovery and reconciliation with the meter register. 5 min
  3. Heat meter data monitoring and reconciliation Read the right heat-meter register, store it with its meter, unit and time, and reconcile the totals with the meter display and the network balance. 11 min
  4. Wired M-Bus commissioning for heat meters Commission wired M-Bus: unit loads, bus voltage, capacitance, primary addresses, telegram records, failure tests and checks against the meter display. 11 min
  5. P1 port guide: DSMR smart meter data How Dutch DSMR and Belgian eMUCS P1 smart-meter ports work, including the RJ12 pinout, telegrams, OBIS codes, commissioning checks and the DSMR6/X1 transition. 8 min
  6. Commissioning 4-20 mA and 0-10 V monitoring Commission analogue signals: loop headroom, scaling, NE 43 fault currents, live-zero voltage, RTD transmitters, sampling and acceptance checks. 10 min

Modbus and RS-485

7 guides · about 52 minutes

  1. Modbus RS-485 commissioning Commission Modbus RTU over RS-485: device parameters, wiring, termination, bias, addressing, decoding, polling, data quality and acceptance checks. 6 min
  2. Modbus TCP vs Modbus RTU Compare Modbus TCP and RTU for existing sites: transport, framing, addressing, port 502, timing, gateways and security. 6 min
  3. RS-485 vs Modbus vs RS-232 RS-485 is an electrical interface; Modbus is a protocol. Compare RS-232 and RS-422, and check the device requirements before connecting. 9 min
  4. RS-485 wiring, termination and bias RS-485 wiring for Modbus RTU: daisy-chain topology, stubs, termination, bias, A/B polarity, common conductor and cable length. 8 min
  5. Modbus register maps: addresses, data types and scaling Read Modbus register maps: holding/input registers, 40001 and zero-based addresses, 32/64-bit values, word order, scaling, status and unavailable values. 7 min
  6. Modbus troubleshooting: timeouts, exceptions and wrong values Diagnose Modbus timeouts, exception 02, incorrect decoded values and frozen readings, with raw RTU frames and timing at 9600 baud. 11 min
  7. Protocol gateway vs transparent bridge Distinguish serial tunnels, Modbus RTU-to-TCP conversion and translation between protocols such as BACnet and Modbus, with tests for each. 5 min

Calculators

All calculators

EpiSensor products

Devices for this topic

Connecting meters that are already installed?

Tell System Builder which meters you have and what interface each one has. It finds the interface product for each meter.

Build a system