Meter interfaces

Pulse outputs, wired M-Bus, Modbus RTU, P1 ports and analogue signals from the meters a site already has.

Most sites already have meters with a pulse output, M-Bus, Modbus or a P1 port. Reading them is often cheaper than fitting new sensors.

Start with the guide for the interface on your meter's label, then use its commissioning checks.

Meter interfaces

6 guides · about 62 minutes

  1. Pulse meters: dry pulse vs active pulse A pulse output meter sends one pulse per fixed quantity of energy, gas or water. Compare dry contact, open-collector, S0 and active outputs, timing and scaling. 14 min
  2. Pulse meter commissioning and reconciliation Commission pulse metering: output circuit, pulse weight, maximum rate, known-count tests, recovery and reconciliation with the meter register. 5 min
  3. Heat metering: how heat meters work and how to monitor their data A heat meter calculates thermal energy from water flow and the flow and return temperatures. How heat metering works, classes, M-Bus or pulse reading. 14 min
  4. Wired M-Bus commissioning for heat meters Commission wired M-Bus: unit loads, bus voltage, capacitance, primary addresses, telegram records, failure tests and checks against the meter display. 11 min
  5. P1 port guide: DSMR smart meter data How Dutch DSMR and Belgian eMUCS P1 smart-meter ports work, including the RJ12 pinout, telegrams, OBIS codes, commissioning checks and the DSMR6/X1 transition. 8 min
  6. Commissioning 4-20 mA and 0-10 V monitoring Commission analogue signals: loop headroom, scaling, NE 43 fault currents, live-zero voltage, RTD transmitters, sampling and acceptance checks. 10 min

Modbus and RS-485

9 guides · about 87 minutes

  1. What is Modbus? How the Modbus protocol works Modbus is a request and response protocol: a client reads and writes numbered registers in a server. Data model, function codes, RTU and TCP frames. 11 min
  2. Modbus RS-485 commissioning Commission Modbus RTU over RS-485: device parameters, wiring, termination, bias, addressing, decoding, polling, data quality and acceptance checks. 6 min
  3. Modbus TCP vs Modbus RTU Modbus RTU vs Modbus TCP in one table: RS-485 or Ethernet, CRC or MBAP header, bus address or IP and unit ID, port 502, timing, gateways and security. 11 min
  4. RS-485 vs Modbus vs RS-232 Is Modbus the same as RS485? No: RS-485 is the physical layer and Modbus the protocol that runs on it. A comparison table, Modbus RTU, and RS-232 vs RS-485. 11 min
  5. RS-485 wiring, termination and bias RS-485 wiring for Modbus RTU: cable, RJ45 and D-sub pinout, daisy-chain topology, stubs, termination, bias, A/B polarity, common conductor and length. 11 min
  6. Modbus register maps: addresses, data types and scaling What a Modbus register map contains and how to read one: the four register types, an example row, 40001 addresses, 32-bit values, word order and scaling. 9 min
  7. Modbus troubleshooting: timeouts, exceptions and wrong values Fix Modbus RTU and TCP timeouts, exception 02, wrong decoded values and frozen readings. Includes timeout arithmetic: 125 registers take 292 ms at 9600 baud. 11 min
  8. Protocol gateway vs transparent bridge Distinguish serial tunnels, Modbus RTU-to-TCP conversion and translation between protocols such as BACnet and Modbus, with tests for each. 5 min
  9. Reading refrigeration controllers over Modbus: Danfoss, Carel and Dixell Serial settings, signed temperature registers and scaling for Danfoss EKC 202, Carel MPXPRO and ir33, and Dixell XR refrigeration controllers. 12 min

More in Meter interfaces